What cable to use (type)

Avatar
Discard
Author Best Answer

NYY: "Nichtmetallischer Mantel, widerstandsfähig gegenüber äußeren Einflüssen" (Non-metallic Sheath, resistant to external influences) - These cables are suitable for outdoor and underground installations and are more resistant to moisture and mechanical stress compared to NYM cables.





For 22kW: Erdkabel NYY-J 5x10 mm²

For 11kW: Erdkabel NYY-J 5x6 mm²


https://www.elektroland24.de/elektroinstallation/kabel-leitungen/erdkabel-nyy-j/erdkabel-nyy-j-5x10-mm2-schnittware-schwarz.html


For the networking cable, 

If the cable is going outside or in direct contact with ground or sunlight, then this cable needs to be used. 


Draka data cable UC900 SS 23, 4 pairs, S/FTP PE, Cat.7


https://www.elektroland24.de/elektroinstallation/kabel-leitungen/netzwerkkabel/draka-datenleitung-uc900-ss-23-4-paare-s-ftp-pe-cat.7.html



Avatar
Discard
Author

Which supply line for a 11 kW wall box?

The minimum cable cross-section for a 11 kW Wallbox supply line with a current of 16 amps is 2.5 mm². However, the recommended average is 6 mm² - also dependent on the cable length. If your supply line is 20 m long, the 2.5 mm² mentioned above are sufficient. With 40 m, however, you should plan for 4 mm² and for up to 70 m 6 mm². Basically, the risk decreases with a larger cable cross-section and your flexibility increases.

Which supply line for a 22 kW wall box?

For a 22 kW Wallbox supply line with a current of 32 amps, the minimum cable cross-section is 4 mm². However, an average of 10 mm² is recommended. The cable length also plays a role here: The cable cross-section of 4 mm² is sufficient for a length of up to 25 m, for 50 m it should be at least 10 mm² and for up to 100 m at least 16 mm². The same applies here: It is better to use a cable that is too thick, as it offers more flexibility.

For comparison: A classic household socket has the same recommendations for the cable cross-section as an 11 kW wall box.

Author

This email template should be used when sending to a customer who would like to prepare the electrical wiring between the metering cabinet and the wallbox location.

Please share the following instructions for the electrician in consideration for installation and planning of the Wallbox we have planned as part of your solar energy system.

The cable should have the following specifications:

For 11kW of wallbox power capacity: Erdkabel NYY-J 5x6 mm²

For 22kW of wallbox power capacity: Erdkabel NYY-J 5x10 mm² (Recommended)

Please leave a minimum of 0.5m of extra cable to the center position of where the wallbox will be planned for installation. For the metering cabinet end of the cable, please leave the cable outside of the metering cabinet, rolled up with enough length to terminate the cable inside of the metering cabinet according to the position of the fuse for the wallbox. The end on the wallbox side should be protected against the weather elements in the event the cable is left outside during pre-construction phase.

All Wallbox offered by Dein Solar can be switched between 11kW and 22kW based on the allowances of the local network provider and ability for your existing electrical cabinet to support the added continuous loads. We recommend installing the larger size cabling in the event the electrical utility allows for a larger capacity wallbox (in future or at the current installation).

For the networking internet cable specifications:

If the networking cable path is to be buried or in contact with outside environment where it’s not protected, we recommend the following cable Draka data cable UC900 SS 23, 4 pairs, S/FTP PE, Cat.7. This cable or a “PE” protected network cable is suitable for use. Please leave a minimum of 0.5m of extra cable at the location of where the wallbox will be installed terminated with a RJ45 connection. The other end should have a RJ45 connection terminated on the end and be in the position next to the house network switch or modem with connection to the internet. The end on the wallbox side should be protected against the weather elements in the event the cable is left outside during pre-construction phase. Please make sure all cables are tested when completed. Test results should be saved using appropriate RJ45 network cable testing equipment.

As a note, the RJ45 connector on the wallbox side could be a reusable connector for the connection as our electrical team will make the final termination according to the final position of the wallbox.

If the cable path is protected, any Cat. 6 cable or higher is suitable for use.

Author

Diese E-Mail-Vorlage sollte verwendet werden, wenn Sie an einen Kunden senden, der die elektrische Verkabelung zwischen dem Zählerschrank und dem Standort der Wallbox vorbereiten möchte.

Bitte teilen Sie dem Elektriker die folgenden Anweisungen zur Installation und Planung der Wallbox mit, die wir als Teil Ihres Solarstromsystems geplant haben.

Das Kabel sollte folgende Spezifikationen aufweisen:

Für 11 kW Wallbox-Leistung: Erdkabel NYY-J 5x6 mm²

Für 22 kW Wallbox-Leistung: Erdkabel NYY-J 5x10 mm² (empfohlen)

Bitte lassen Sie mindestens 0,5 m zusätzliches Kabel zur Mittelposition, an der die Wallbox installiert werden soll. Am Ende des Kabels im Zählerschrank lassen Sie das Kabel bitte außerhalb des Schranks aufgerollt, mit ausreichender Länge, um das Kabel im Schrank gemäß der Position der Sicherung für die Wallbox zu beenden. Das Ende an der Wallbox-Seite sollte gegen Witterungseinflüsse geschützt sein, falls das Kabel während der Vorkonstruktionsphase im Freien gelagert wird.

Alle von Dein Solar angebotenen Wallboxen können je nach Zulassung des örtlichen Netzversorgers und der Fähigkeit Ihres vorhandenen Elektroschranks, die zusätzlichen Dauerlasten zu unterstützen, zwischen 11 kW und 22 kW umgeschaltet werden. Wir empfehlen, das größere Kabel zu installieren, falls der Elektrizitätsversorger eine Wallbox mit größerer Kapazität zulässt (in Zukunft oder bei der aktuellen Installation).

Für die Netzwerkkabel-Spezifikationen:

Wenn der Netzwerkkabelweg vergraben oder in Kontakt mit der Außenumgebung sein soll, wo er nicht geschützt ist, empfehlen wir folgendes Kabel: Draka Datenkabel UC900 SS 23, 4 Paare, S/FTP PE, Cat.7. Dieses Kabel oder ein "PE"-geschütztes Netzwerkkabel ist geeignet. Lassen Sie mindestens 0,5 m zusätzliches Kabel an der Stelle, an der die Wallbox installiert werden soll, und beenden Sie es mit einer RJ45-Verbindung. Das andere Ende sollte mit einer RJ45-Verbindung abgeschlossen sein und sich neben dem Hausnetzwerk-Switch oder Modem mit Internetverbindung befinden. Das Ende an der Wallbox-Seite sollte gegen Witterungseinflüsse geschützt sein, falls das Kabel während der Vorkonstruktionsphase im Freien gelagert wird. Stellen Sie bitte sicher, dass alle Kabel getestet sind, wenn sie fertiggestellt sind. Testergebnisse sollten mit geeigneten RJ45-Netzwerkkabel-Testgeräten gespeichert werden.

Als Hinweis könnte der RJ45-Stecker auf der Wallbox-Seite ein wiederverwendbarer Stecker für die Verbindung sein, da unser Elektroteam die endgültige Anbindung entsprechend der endgültigen Position der Wallbox vornehmen wird.

Wenn der Kabelweg geschützt ist, ist jedes Cat. 6-Kabel oder höher geeignet.

Best Answer

Which supply line for a 11 kW wall box?

The minimum cable cross-section for a 11 kW Wallbox supply line with a current of 16 amps is 2.5 mm². However, the recommended average is 6 mm² - also dependent on the cable length. If your supply line is 20 m long, the 2.5 mm² mentioned above are sufficient. With 40 m, however, you should plan for 4 mm² and for up to 70 m 6 mm². Basically, the risk decreases with a larger cable cross-section and your flexibility increases.

Which supply line for a 22 kW wall box?

For a 22 kW Wallbox supply line with a current of 32 amps, the minimum cable cross-section is 4 mm². However, an average of 10 mm² is recommended. The cable length also plays a role here: The cable cross-section of 4 mm² is sufficient for a length of up to 25 m, for 50 m it should be at least 10 mm² and for up to 100 m at least 16 mm². The same applies here: It is better to use a cable that is too thick, as it offers more flexibility. 