Example project: Gasse

We went on site to comission the system but it didn't pair the optimizers. As it was late and winter, we decided to do the pairing remotely later on when there's more light. When trying this, the pairing process failed and the DC voltage on the inverter indicated 0 V.


How did we figured out what the issue was? What were the steps we had to do in order to a) find out and b) resolve the issue?

Avatar
Discard
Best Answer

Before:

Inverter indicating OV DC - this means strings are not connected to inverter or there is wrong wiring polarity.

image2

Checking on the GAK wiring you can see if wires are connected properly (even if string voltage is good on roof).


Always need to check where wires should be connected on labels. In this case wires were connected wrong.


After:

Need to make sure string voltage is checked and positive wire is connected in proper place. Positive wires will be on one side, negative other side.\

When polarity is correct, inverter will pair and produce


Avatar
Discard
Author Best Answer

One can see in the picture that they have labeled the black cable with + and the red with minus, which was not correct.


When measuring the voltage, the red wire was +24 V (24 optimizer) and the black wire was minus.

This is how it should have been done: